Runing water=heater from generator.

Posted by trysquire (My Page) on
Sun, Jul 26, 09 at 23:57

Re: Electric water heaters. An additional thought regarding reducing the load placed on your generator when powering an electric water heater.
As mentioned before if you disconect the uper element, then the power draw would be half normal, and the heating time would be TWICE NORMAL.

If you have two heating elements (almost all water heaters have two heating elements) and you rewire them in series (perferably by means of a high power rated (double pole doubel throw) switch that is hiden so no one (like a kid) throws it and puts the water heater back into full wattage) you can reduce the load to one fourth that of normal. The heating time will be FOUR TIMES NORMAL.

Also note that if your water heater is a 240 volt unit and you run it on 120 volts, the power the heater would draw would be only 1/4 of normal. The heating time would be FOUR TIMES NORMAL. This is because at 120 volts the curent draw would be half that of normal. And since the voltage is only 120 (half that of normal) and the wattage is AMPS x VOLTS the wattage draw would be 1/2 x 1/2 = 1/4. This is if you ran a 240 volt water heater on 120 volts and left both heating elements conected.

If you ran a 240 volt water heater on 120 volts and you disconected the uper element then the power draw would be 1/8 that of normal. The heating time would also be EIGHT TIMES NORMAL.

If you were to put two 240 volt elements in series and run them on 120 volts the power draw would be 1/16 normal. The heating time would be 16 TIMES NORMAL. This is geting a bit long and might not be enough when adding on heat loss to ambient. However if you realy want to cut back on power draw and you can get by with very long hot water tank recovery time (not too many people using the hot water) this might be worth a try.

Reducing the power draw might be raealy valuable since it would allow you to use a small generator that gets many hours from one gallon of gas such as the HONDA eu2000i .

I have gas hot water. If I had electric I would try the reduced wiring and after determining which worked best for my requirement I would install a hiden switch with a long life low power draw indication light in plain view that would remind me to turn it back to full power when once again runing from the grid. You would require a three pole double throw high power switch (hard to find) so you would have a pole for the light.

Signed: Trysquire


Follow-Up Postings:

 o
RE: Runing water=heater from generator.

Most dual element hot water heaters turn only one element on at a time anyway.


 o
RE: Runing water=heater from generator.

Each element is on a seperate thermostatic switch. If enough water is drawn from the water heater both elements will come on at the same time. If both elements drawing power excedes the capacity of your generator the circuit breaker of the generator will trip, if you are lucky. But these circuit breakers are not very reliable. It is just as likley that over-loading a generator will damage it.

This is the whole reason to do this re-wiring in the first place.


 o
RE: Runing water=heater from generator.

Why did it take you over a year to respond ? Roflmbo !


 o
RE: Runing water=heater from generator.

It took over a year to respond because the original text was copied and posted on a new thread, and everytime I looked at this site I went to the original thread that has much more about generators on it.


 o
RE: Runing water=heater from generator.

trysquire, Modern water heaters do not run both elements simultaneously. Even when all the water in the tank is cold the water heater uses only one element at a time.
ewalk, The reason it took him so long to respond: His electronic calendar/clock is wired in a series with his twin element 240v water heater running on 120 volts. Hence the fact that he is about a year behind. (Joke, ha,ha)


 o
RE: Runing water=heater from generator.

Ray: That would explain the Lapse lol .


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Tool Shed Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here