line size for yard hydrants

Posted by bob.green colorado (My Page) on
Sun, Mar 31, 13 at 10:15

Am going to install a PE water line to feed 4 yard hydrants, tie-in at the the house service line. I have about 65psi @ the meter, will run approximately 410 feet and drop about 13 ft vertically to the bottom hydrant. Will have no more than 2 hydrants on at any given time. What size line should I use?
Thanks,
Bob


Follow-Up Postings:

 o
RE: line size for yard hydrants

An addition to my first post yesterday, March 31...I am trying to decide whether to use 3/4" or 1" polyethylene underground pipe.
Thanks,
Bob


 o
RE: line size for yard hydrants

For the relatively small difference in cost, I would go with the 1" poly. You will not lose much pressure by doing this. Also, nothing worse than going with a smaller pipe only to find out after you have it in that you do not have the pressure that you had expected. Once and done.


 o
RE: line size for yard hydrants

bg,

Are the hydrants going to be just hoses or actually uses to irrigate areas? The first information you find out is what flow rate you are getting from your main line. You already know the pressure. Install your tee at the mainline then install a ball valve shut off. Attach a small length of your poly line and time filling up a 5-gallon bucket. Calculate your gallons per minute source. That flow rate will be at each hydrant and if you use two hydrants at the same time, each will have half of that rate. If you have all 4 hydrants working, each will have a quarter of the total flow rate. Friction loss along the pipe increases as the pipe diameter gets smaller. For over 400 lf you should use a 1 1/2" diameter to minimize pressure loss. This will decrease the noise of the water traveling thru smaller pipe diameters and eliminate water hammer when valve are shut quickly. This is because the water velocity in the pipe decreases as the pipe diameter increases. The 13 ft vertical drop to the last hydrant will increase pressure by 6 psi which is good but not alot. All these comments are general in nature and not to be considered exact. JMHO anyway. Aloha


 o
RE: line size for yard hydrants

Thank you all for your advice and info. I have been doing some calculations over the last few days and came up with the same solution as you - will go with 1".
Bob


 o Post a Follow-Up

Please Note: Only registered members are able to post messages to this forum.

    If you are a member, please log in.

    If you aren't yet a member, join now!


Return to the Irrigation Forum

Information about Posting

  • You must be logged in to post a message. Once you are logged in, a posting window will appear at the bottom of the messages. If you are not a member, please register for an account.
  • Please review our Rules of Play before posting.
  • Posting is a two-step process. Once you have composed your message, you will be taken to the preview page. You will then have a chance to review your post, make changes and upload photos.
  • After posting your message, you may need to refresh the forum page in order to see it.
  • Before posting copyrighted material, please read about Copyright and Fair Use.
  • We have a strict no-advertising policy!
  • If you would like to practice posting or uploading photos, please visit our Test forum.
  • If you need assistance, please Contact Us and we will be happy to help.


Learn more about in-text links on this page here