erratic voltage at the controller

copelt
14 years ago

I have a 12 zone Hunter Pro C with Irritrol valves. I have erratic controller voltage and my valves are behaving oddly with only #10 working. I tested 3 solenoids at the controller - they are good. I am not getting voltage at the valves except for #10. The controller seems to be trying to run zones simultaneuosly, but even those that have normal voltage like #9 (I think) don't operate. Is this a wiring problem (no digging done recently) or a controller problem?

Here is each of my zones set to run followed by voltage for every zone output at the controller. Readings are stable unless noted otherwise.

#1 28,28,28,28,28,26,4,0,0,0,28,.5

#2 28,28,28,28,28,26,4,0,0,0,28,.5

#3 26,26,26,26,26,23,4,0,0,0,26,.5

#4 26,26,26,26,26,25,4,0,0,0,26,.5

#5 26,26,26,26,26,25,4,0,0,0,26,.5

#6 8,8,8,8,8,26,2,0,0,0,9,.2 - zones 1-5 very jittery

#7 .4,.4,.4,.4,.4,.7,26,0,0,0,.4,0

#8 .4,.4,.4,.4,.4,.7,.7,26,0,0,.4,0

#9 .3,.3,.3,.3,.3,.6,.6,0,26,0,.4,0

#10 .2,.2,.2,.2,.2,.5,.7,0,0,26,.3,0

#11 26,26,26,26,26,23,4,0,0,0,26,.5

#12 .3,.3,.3,.3,.3,.7,.7,0,0,0,.4,26